This area is visible if the Bypass Enable option is set in CONTROL_OPTS (typically when the PID block is a slave in a cascade pair). Bypass makes the output value equal to the % SP value, which allows the master loop to drive the output if the transmitter is unavailable. When the block is in MAN or OOS mode, click Bypass to turn Bypass on. Click Normal to turn off Bypass.
In the PID function block, BYPASS is used when the control function block is a slave block in a cascade. If a transmitter failure or some other problem occurs that causes the slave controller to see a Bad input signal, BYPASS can be activated so that the signal coming from the master controller passes through the slave to the field. In this manner, the loop still has some control; however, dynamic performance will suffer because a cascaded loop has effectively been replaced with a single PID.作者: celanese刘威 时间: 2016-11-5 19:18