标题: Link mater device求解! [打印本页]

作者: celanese刘威    时间: 2016-10-25 20:56
标题: Link mater device求解!
primary link master 就是H1 card?
当H1card 实效 link master device 能起作用吗?


作者: 舞长安    时间: 2016-10-25 21:36
A Link Master device controls when devices access the fieldbus and executes the link schedule which synchronizes communications with function block execution on the fieldbus.
The H1 card or any field device that supports Link Master functionality can function as a Link Master device.
Only one Link Master device can be active at a time on the fieldbus segment. This device is called the LAS.
The DeltaV system can configure one Link Master device to function as the primary Link Master device.
When the primary Link Master device is attached to the fieldbus, it takes over as the LAS.
The H1 card always functions as the primary Link Master.
When the H1 card is redundant, the secondary H1 functions as the primary Link Master if the primary H1 card fails.
All other Link Master devices are backup Link Master devices that can take over as LAS only if the primary Link Master device fails.
One backup Link Master field device is supported per fieldbus segment. The fieldbus devices communicate on a schedule (executed by the LAS) as required to implement the control strategy.

作者: celanese刘威    时间: 2016-10-25 21:47
舞长安 发表于 2016-10-25 21:36
A Link Master device controls when devices access the fieldbus and executes the link schedule which  ...

非常感谢您!另外这个在组态的过程中需要主动去设置吗?还是DeltaV默认H1卡就是primary link master同时网段上的地址为20的表就是link master device?
作者: 舞长安    时间: 2016-10-25 22:02
celanese刘威 发表于 2016-10-25 21:47
非常感谢您!另外这个在组态的过程中需要主动去设置吗?还是DeltaV默认H1卡就是primary link master同时 ...

Link Master:controls when devices access the fieldbus and executes the link schedule which synchronizes communications with function block execution on the fieldbus.Link Master devices are capable of taking over as LAS if the Primary Link Master device fails.
The backup Link Master must use address 20.


作者: celanese刘威    时间: 2016-10-25 22:08
舞长安 发表于 2016-10-25 22:02
Link Master:controls when devices access the fieldbus and executes the link schedule which synchron ...

thank you very much! would you like sends me your weixin count ?
作者: 舞长安    时间: 2016-10-25 22:11
celanese刘威 发表于 2016-10-25 22:08
thank you very much! would you like sends me your weixin count ?

有Delta V问题来这里,基本、应该能解决吧。这里也有好多Delta V的资料,你可以去资料区看看。

作者: tianyuww    时间: 2016-10-26 16:11
此功能主要用于管理FF链路,在所有系统硬件正常的时候,H1卡是master,然后segment模块上链接的设备(此功能支持的设备),启用Link Master功能作为备用(在新建设备时候进行设置,将ID等级选择为20),这样当H1卡有问题时候,被启用了backup link master的设备就可以自动切换。具体为同一个segment 上的Devices 跟卡及控制器,以及device间的通讯是需要时间分配的,因为是一条cable连接着他们。管理时间分配的是这个 las,H1卡在作为master的时候,它就是las,但是除了卡以外,每个segment上还允许定义一个device作为backup las,当H1卡件fail 的时候,这个device就充当 las 管理时间分配。

Fieldbus block 是可以assign 到 device 上运行的,可以不在控制器里运行,理论上一个 segment 上的 device之间是可以继续通讯工作的,比方说 pid 的 ai,ao,pid都可以在FF device 上运行,pid 的控制是可以不需要deltav来管理,这个只是对单个回路或者是 assign 在同一个 segment 的 device就可以单独完成的控制逻辑。设置成在 FF里,好处是可以减少通讯。 经典是 pid回路,就不需要一直把 ai 值传到控制器,控制器计算ao,再通过通讯跟ao block再传到 device。通过带有FF的功能块,将DST连接到block上,然后再下装后,就可以实现此功能。

作者: 小明    时间: 2019-3-21 15:12
学习学习
作者: zhangyili    时间: 2019-12-19 20:13
不错,就这个备用的调度器功能。在H1卡上或找个AI的变送器都可以做BLAS